I have a Coachmen 2002 Mirada in a 2001 F53 ford chassis. The dashboard air is not working. It is an Evans Tempcon "3 dial" system with a Ford compressor. Not sure how to proceed.
Symptom: When set to MAX with the blower in 1 it blows warm air. The compressor clutch does not engage.
What I have checked: I have verified 12v from the switches to the pressure switch. The pressure switch is open.Several times it engaged the clutch momentarily then it opened and stopped it. I have checked the thermostat and it is open at ambient temp 89f. It is possible that the thermostat stopped the system from working when it quit.
I connected the clutch to 12v at the pressure switch harness and it does come on.
I have connected a manifold and got the readings of 100 on both sides without the compressor running and 5 low and 110 high with the compressor on.
When the clutch ir engaged manually there is no difference in the temperature of the at at the vents.
While learning to use the manifold (sort of) I inadvertantly opened the valves and noticed that the fluid was a tan color. I don't know if this is oil or contamination.
History: About a year ago I lost all fluid because the low pressure hose was cut by the edge of the radiator. Bad routing from the factory. I repaired the hose. I could not replace it because the bolt holding the tube to the compressor had frozen solidly to the tube. I also replaced the drier with a generic replacement. I drew a vacuum of 29 and left it for several hours to check leaks and then ran it to evaporate water. I filled it with 2.5 lbs of 134 and it worked great for an entire year including 6 weeks out west and a 2 week evacuation from Irma in Georgia. It sat for a month then when I tried to use it it did not work and had been sitting ever since. I did try some stupid things. I released some fluid. What was I thinking? I tried adding 12 oz to replace that.
Present: I do not know how much R134 there is in it now or if it might have leaked somewhat over time. It has been suggested that I may have a leaking drier or a worn out compressor. I did finally find the label with the system information which was up on the evaperator housing. It takes 2.75 lbs rather than the 2.5 that I had found in online specs.
1 Is that brown color a problem or just compressor oil?
2 Should I try having it emptied then refilling it correctly and trying again or should I assume the compressor is toast and replace it right away.
3 Do I need to flush it? Since a lot of the fittings are frozen that would be rough to do properly.
4 How much oil will I need to add if I refill it with the same compressor but a new drier?
I have a new drier on order along with plain R134. I have compressor oil. I have ordered the thermostat. Anything else I need?
I really appreciate anything you can tell me. I am learning but this is out of my comfort zone. I am mechanically able to handle most things but AC is not simple.
Symptom: When set to MAX with the blower in 1 it blows warm air. The compressor clutch does not engage.
What I have checked: I have verified 12v from the switches to the pressure switch. The pressure switch is open.Several times it engaged the clutch momentarily then it opened and stopped it. I have checked the thermostat and it is open at ambient temp 89f. It is possible that the thermostat stopped the system from working when it quit.
I connected the clutch to 12v at the pressure switch harness and it does come on.
I have connected a manifold and got the readings of 100 on both sides without the compressor running and 5 low and 110 high with the compressor on.
When the clutch ir engaged manually there is no difference in the temperature of the at at the vents.
While learning to use the manifold (sort of) I inadvertantly opened the valves and noticed that the fluid was a tan color. I don't know if this is oil or contamination.
History: About a year ago I lost all fluid because the low pressure hose was cut by the edge of the radiator. Bad routing from the factory. I repaired the hose. I could not replace it because the bolt holding the tube to the compressor had frozen solidly to the tube. I also replaced the drier with a generic replacement. I drew a vacuum of 29 and left it for several hours to check leaks and then ran it to evaporate water. I filled it with 2.5 lbs of 134 and it worked great for an entire year including 6 weeks out west and a 2 week evacuation from Irma in Georgia. It sat for a month then when I tried to use it it did not work and had been sitting ever since. I did try some stupid things. I released some fluid. What was I thinking? I tried adding 12 oz to replace that.
Present: I do not know how much R134 there is in it now or if it might have leaked somewhat over time. It has been suggested that I may have a leaking drier or a worn out compressor. I did finally find the label with the system information which was up on the evaperator housing. It takes 2.75 lbs rather than the 2.5 that I had found in online specs.
1 Is that brown color a problem or just compressor oil?
2 Should I try having it emptied then refilling it correctly and trying again or should I assume the compressor is toast and replace it right away.
3 Do I need to flush it? Since a lot of the fittings are frozen that would be rough to do properly.
4 How much oil will I need to add if I refill it with the same compressor but a new drier?
I have a new drier on order along with plain R134. I have compressor oil. I have ordered the thermostat. Anything else I need?
I really appreciate anything you can tell me. I am learning but this is out of my comfort zone. I am mechanically able to handle most things but AC is not simple.